Fault 3P HV F27

DC_Insulation_Fault

DC insulation impedance fault

Academy field checklist (DC_Insulation_Fault) — no EcoBSS service-table row for this bit.

Register map

Family
Three-phase HV
Register
556
Bit
10

Field checks

  1. Same insulation hunt as F2: megger strings, dry connectors, PE integrity.
  2. High humidity mornings can trip — retest when dry before condemning hardware.
  3. Contact Inversol if the fault returns after a clean power cycle.

FAQ

What does EcoBSS F27 mean?
DC insulation impedance fault
What should I check for EcoBSS F27?
  1. Same insulation hunt as F2: megger strings, dry connectors, PE integrity.
  2. High humidity mornings can trip — retest when dry before condemning hardware.
  3. Contact Inversol if the fault returns after a clean power cycle.
When should I contact Inversol?
Confirm LV vs HV family on the nameplate, complete the field checks, then contact Inversol with model, SN, family, and a photo if the code returns after a clean power cycle.