AC_NoUtility_Fault

No utility / grid voltage at AC terminals

Academy field checklist (AC_NoUtility_Fault) — no EcoBSS service-table row for this bit.

Register map

Family
Three-phase HV
Register
557
Bit
2

Field checks

  1. Measure GRID terminal voltage; confirm upstream breaker / isolator is closed.
  2. If off-grid is intentional, check mode settings so the unit is not waiting for utility.
  3. Contact Inversol if the fault returns after a clean power cycle.

FAQ

What does EcoBSS F35 mean?
No utility / grid voltage at AC terminals
What should I check for EcoBSS F35?
  1. Measure GRID terminal voltage; confirm upstream breaker / isolator is closed.
  2. If off-grid is intentional, check mode settings so the unit is not waiting for utility.
  3. Contact Inversol if the fault returns after a clean power cycle.
When should I contact Inversol?
Confirm LV vs HV family on the nameplate, complete the field checks, then contact Inversol with model, SN, family, and a photo if the code returns after a clean power cycle.

Partner lookup from EcoBSS Flex register map V1.2 — not a substitute for the official service manual or live measurements. Always match the inverter family (3P LV / FLEX 3L vs 3P HV).