Fault 3P LV F30

AC_MainContactor_Fault

AC main line contactor fault

Academy field checklist (AC_MainContactor_Fault) — no EcoBSS service-table row for this bit.

Register map

Family
Three-phase LV (FLEX 3L)
Register
556
Bit
13

Field checks

  1. Field-check the main AC line contactor the same as F11 (coil, feedback, welding).
  2. Confirm upstream breaker is closed and voltage is present at the contactor input.
  3. Contact Inversol if the fault returns after a clean power cycle.

FAQ

What does EcoBSS F30 mean?
AC main line contactor fault
What should I check for EcoBSS F30?
  1. Field-check the main AC line contactor the same as F11 (coil, feedback, welding).
  2. Confirm upstream breaker is closed and voltage is present at the contactor input.
  3. Contact Inversol if the fault returns after a clean power cycle.
When should I contact Inversol?
Confirm LV vs HV family on the nameplate, complete the field checks, then contact Inversol with model, SN, family, and a photo if the code returns after a clean power cycle.

Error won't clear? Send a photo of the display to WhatsApp +995 568 999 668: an Inversol engineer will tell you what to check.