Fault F20

Tz Dc OverCurr Fault

Off-grid DC overcurrent fault

Deye service: Tz Dc OverCurr — off-grid inrush on backup.

Field checks

  1. Reduce inrush currents of loads fed from the backup port in off-grid mode.

If the hybrid restarts many times in production hours with no code, check the DC side the same way as on F24 (insulation and connectors).

For DC / PV checks see solar panels and the inverter hub.

FAQ

What does Deye F20 mean?
Hardware DC overcurrent. On site: off-grid start with a large load, an overloaded string, or an MPPT path.
How do I tell array from inverter on F20?
Swap PV1 and PV2. If the fault follows the string, fix the array. If it stays on the same tracker, write service with voltages and a photo.
Is F20 always a broken MPPT?
No. Reduce the off-grid start load first. Many cases clear without a board change.

Error won't clear? Send a photo of the display to WhatsApp +995 568 999 668: an Inversol engineer will tell you what to check.