Fault F18

HW AC OverCurr Fault

Hardware-level AC overcurrent fault

Deye service: HW AC OverCurr — same AC overcurrent path as F15.

Field checks

  1. Check LOAD and GRID output lines for short circuits.
  2. Disconnect heavy loads and restart the unit.

A short inrush on LOAD is often enough to trip the hardware path. That is a load-path issue, not a first-day board swap. If F18 stays after the path is corrected, continue on F34 (overload or short on LOAD).

For this AC-side class see Deye hybrid inverters in Georgia and size a kit in the system constructor.

FAQ

What does Deye F18 mean?
Hardware AC overcurrent. On site it often follows a large inductive start on LOAD after the grid returns.
What should I check first for F18?
Move heat pumps and compressors off LOAD onto GRID (with CT if used). Restart. Read the 7-day log.
When is F18 not a hardware defect?
When it appears only at inductive start on LOAD, especially after grid return, and clears after those loads are taken off LOAD.

Error won't clear? Send a photo of the display to WhatsApp +995 568 999 668: an Inversol engineer will tell you what to check.

Installer or service company? Deye, ECOBSS and Heckman equipment: partner prices on request via WhatsApp.