Fault F55

DC Voltage Too High

Dangerously high DC voltage

Deye service: DC Voltage Too High — same Voc path as F32.

Field checks

  1. Measure PV string voltage.
  2. Reduce series modules until voltage is within the safe operating window.

In cold weather the open-circuit voltage of panels rises, so a string that is fine in summer can exceed the limit on a winter morning.

For DC / PV checks see solar panels and the inverter hub.

FAQ

What does Deye F55 mean?
DC bus voltage too high: battery or PV voltage above the limit, often a PV string that is too long in the cold.
What should I check first for F55?
The string Voc at the lowest site temperature against the MPPT maximum voltage, and the battery charge voltage setting.
When do I write Inversol for F55?
When the string voltage is within the limit, the charge voltage is correct and the code stays. Send a photo, the string layout and the battery settings.