Fault F35

AC NoUtility Fault

No grid utility voltage detected

Deye service: AC NoUtility Fault — GRID present? main breaker?

Field checks

  1. Confirm utility voltage is present at the AC infeed.
  2. Check the position of the incoming grid breaker / isolator.

If the grid returns and the code clears, the cause was the grid or the breaker. With frequent outages check whether one phase is dropping out.

For this AC-side class see Deye hybrid inverters in Georgia and size a kit in the system constructor.

FAQ

What does Deye F35 mean?
No AC grid: the grid is missing, a protection tripped or a phase is lost. It is not listed in the hybrid-series manual, so check the manual for your model.
What should I check first for F35?
Measure L1–L3 and N on the GRID terminals and check the breaker before the inverter.
When do I write Inversol for F35?
When GRID voltage is normal, the breaker is on and the code stays. Send a photo and the model.